Originally Posted by HotLine1
Just an FYI, there are some inspectors that have an issue with the two (2) conductors under the acorn. That is IF the #6 is not a continuous piece. AFAIK the acorn is not listed for multiple conductors.

That said, although we all have come upon a lot of 'conductors' under the acorn, be it telco, cable, dish, etc.

Nope. One per acorn. Go to your truck and get another one for another wire. That is why I said it is probably cheaper to just loop the wire through. That is the same as trying to get 2 wires in a breaker with a single wire lug. One of them is not getting proper clamp pressure. There are clamp type connectors that are listed for multiple wires (multiple holes) but a lot of them are not listed for burial.


Greg Fretwell