ok so here is the wires etc. as they are now,
the pole has a meter on it, right under that is a 200 amp line that is in pvc and leads to a 200 amp transfer switch about 100 feet from the pole, (cutler hammer/eaton DT363URK, the switch is a simple on off on, 3 wires go in this switch, and then in the middle position it is off, move the handle up its then connected to the generator, move the handle down its connected to the line from the pole. there no nothing hooked to the generator side at all. right next to the transfer switch is a midwest electric terminal box, that box that has a wire from the transfer switch, then the terminal box feeds 2 buildings each with100 amp breaker boxes, and the house 20 amp breaker box.
its all 3 wire, and was installed over 10 years ago, there is no 4 wire anyplace. i thought about doing the main disconnect outside the main building ( where the pole power line goes and the transfer switch is) but if its under the meter on the pole lit would be so much more easy. all is a 3 wire set up. i know that if the pole breaker has a main disconnect then its all 3 wire feeder downline. this was a common set up for solar power a few years back in my area. so i cant dig up all this wire and replace it with a 4 wire, the install was code at the time, yes i know but it was. it works fine and causes no problems.
so how do i make it work with a pole mounted breaker disconnect? i have seen so many electric coop drawings on line for excatly what i am describing. meter- pole mount breaker box, then feeds the house etc.
,
please give me your iinput.
thank you