HI
i really must be in the twilight zone with the local inspectors or they just really want to mess with me, so i asked the older inspector if i could just put a 200 amp single breaker outdoor right under the only meter on the pole (main conductor) and then everything is protected down the line, treat it like feeders, the 3 wire cable is there and travels 50 feet to the house, he said yes but... that wont solve my terminal box in the basement, he said as soon as it comes into the terminal box, you have to 4 wire it over to each panel from there.

i cant do 4 wire from the future breaker box on the pole to the terminal box in the basement, i would have to dig up all old wire, way to much work, so as long as a separate the neutral and the ground in the new terminal box in the basement and make it all 4 wire in that box and then feed wire to each panel 4 wire, i should be ok and in code right? then do i need pvc for physical protection or just as long as its under sheetrock????this is the easy way for me to do this. comments please!