The FIRST issue is whether the fire pump is deemed auxiliary or life-safety – essential and critical.
If you don't know that status, then you can't begin your design.
Auxiliary fire pumps are installed because the fire insurance company gives the facility a nice price break on insurance. Such an installation provides FULL performance in the sprinkler array. Any fire gets snuffed out QUICK. This is deemed essential (on the economics) if, say, a warehouse is loaded with inflammable goods. (furniture storage, ...)
An essential and critical life-safety fire pump is not oriented towards goods – just people. Any structure that is sure to hold very large numbers of the general public is held to this standard. This is why all new football stadiums are built out of steel and concrete. A century ago, the norm was wood; it's so much cheaper and quicker to erect.
If the design is held to the higher standard, then the prime mover (engine) for the fire pump gets bumped up. How much it gets bumped is usually outside the NEC. Your Fire Marshall is the AHJ. There's really nothing we can say about it.
The folks that build fire pumps usually have a pretty solid handle on what's involved – and are your best design source.
Typical issues don't even turn on conductor sizes, which most guys figure pretty quick. Instead, RACEWAYS are the issue. These systems are VERY picky about protecting the conductors. Generally they have to be encased in concrete and rigid metallic conduit (long runs) – or buried in rigid non-metallic conduit or rigid metallic conduit, exposed.(limited distances, ask AHJ) The only exception to this is the final whip to the motor, itself. That will be in Sealtite.
Other BIG issues turn on how you're going to enter the frame of the fire pump controller – and getting the voltage right. (208Y120 is NOT acceptable for a 240V rated controller and pump. This trips up MANY.)
Getting underground conduits in before the slab is poured can save you an ocean of money.
&&&
As for your conductor math – it looks way off. C/Bs for fire pumps are set at melt-down levels. So a 200A normal draw (3/0-4/0 conductors, distance de-rated) is mated with a 1200A C/B. The disconnecting means is used for service purposes only. So in this case, the switch would be a 200A frame size beast. (NEMA1 or NEMA3R)
Unless you run a LOT of RMC, stay with thread-less connectors. Yes, they are very expensive. They are also virtually idiot proof.
Plan on EVERY auxiliary circuit being in RMC, too. Figure on a jockey pump circuit and service lighting, a GFCI or two. These can tap the same Fire Pump Service – but must do so far enough ahead to make service calls on the pump controller possible. (when the controller is de-energized) Buchanan has K-taps that are often used to feed a SDS in such layouts. If this is done, figure on another fused disconnect – just for the auxiliary circuits. Figure ona Sparately Derived Service. (480Y277 Service MAIN ==> 208Y120 sub-panel; or 480V ==> 240/120V single phase (center) tapped SDS. The loads are so trivial that single phase is common; jockey pumps are typically 240-208V.
The gen-set is expected to be co-located. But it's not an absolute requirement. If it's any distance away, then you're destined to be using the same (underground/ under-slab) raceways as above.
The gen-set is also going to have issues such as: block heater – engine warm 100% of the time; Diesel fuel (never gasoline) – the tank sized to run X minutes – natural gas is expected to be cut-off. (earthquake/ terrorism/ collision/ jet impact (9-11), etc. )
It's control circuits will also get the full raceway treatment. You'll have to attain cleanances all around the gear -- any and all of it -- so that the service personnel can do their thing without touching the field conductors. Beware.
A regular engine run test will be mandated by the AHJ if the system is deemed life-safety critical.
So, as you can see, the status of the fire pump dictates a slew of design issues that are NOT in the NEC. So stop looking there. It's a total waste of your time.
The guy who's going to really design your system is the AHJ. He'll lay out the broad strokes. THEN you can get to work. You want plenty of lead time to get your underground raceways in place – dead on!
You want to enter the fire pump controller in an approved manner. No, you can't enter the chassis any way you want, anywhere you want. You'll need exact cut-sheets for it.
The mechanical layout of the fire pump is essential. Watch out, those boys can hold their stuff back – to leave you scrambling to do your thing.
Your general installation standards will be right up there with elevator control rooms: super picky.
Fire pumps (essential life-safety critical) are as difficult as Division 1 chemical plants. Nothing will be fast, easy or cheap. They are designed for WWV and the Apocalypse.
Auxiliary fire pumps are only a tad easier. The only major difference being gen-set sizing. BTW, MOST of the fire pumps (in commercial locations) are auxiliary fire pumps.
You would be extremely wise to get a j-man on your job who has been down this road before -- a top notch j-man.