GE just started making arc faults that work with shared neutrals. I couldn't figure out how to link this so I cut and pasted it. This is no help to the OP unless he adds a small sub panel, but I expect the other manufacturers will follow suit.





Combination Arc Fault Circuit Interrupters
Application Guidelines
Applying 1-pole Combination AFCIs to Shared Neutral Circuits
Until now, using a shared neutral (multiwire branch circuits) on arc fault protection circuits required the
use of 2-pole AFCI breakers, since the AFCI circuitry uses a ground fault CT to help it detect arcs. But
with GE’s newly developed combination AFCI technology, no ground fault CT is required, so shared
neutral circuits can be used with two 1-pole AFCIs connected together with a handle tie (see Figure 1).
The use of shared neutral circuits produces significant copper savings when two branch circuits are
close to each other but far from the circuit breaker panel. A shared neutral circuit uses 3-conductor
NM-B wire to join two adjacent circuit breakers in the panel to a junction box near the branch circuit
loads/outlets (see Figure 2).
GE
Electrical Distribution
imagination at work
Figure 1.
Two 1-pole AFCIs with
THT104 handle tie
Figure 2.
Wiring diagram
AFCI
Panel
AFCI
12/14-3 NM-B
12/14-2 NM-B
12/14-2 NM-B
Junction box
Branch
circuit #1
(A-phase)
Branch
circuit #2
(B-phase)
AFCI pigtails
Red conductor
Note: for simplicity the ground wires are not shown
White conductor
Black conductor
Neutral bar
DET-719 (11/09)
Information provided is subject to change without notice. Please verify all details with GE. All values are design or typical values
when measured under laboratory conditions, and GE makes no warranty or guarantee, express or implied, that such performance
will be obtained under end-use conditions.
Applying 1-pole Combination AFCIs to Shared Neutral Circuits
Selection
The catalog numbers for new combination type AFCIs that are suitable for use in shared neutral
circuits are shown below. It is important to note that the MOD 3 suffix be on the breaker, as the MOD 2
suffix type AFCIs do have ground fault CTs and cannot be used in shared neutrals. MOD 3 breakers
are easily distinguishable by their gray cases and black test switches.
Installation
Connecting two 1-pole Combination AFCIs to a shared neutral circuit is easy. Before inserting the
AFCIs into the panel, connect the handles together with the handle tie (Cat. No. THT104). Then, as
shown in Figure 2, connect the black conductor to the load lug of the first AFCI and connect the red
conductor to the load lug of the second AFCI. The white conductor can be connected to the neutral
lug of either AFCI. It is not necessary to wire the two neutral lugs together. The second AFCI’s neutral
lug can remain unconnected.
The handle ties only provide manual on-off capability between one-pole devices. They do not tie the
internal trip mechanisms together. Therefore, after installation and energization, both of the AFCI’s
push-to-test switches should be tested in both the up and down positions.
This application complies with all applicable National Electric Codes and UL standards.
Amps 10kAIC Plug-In 22kAIC Plug-In 10kAIC Bolt-On 22kAIC Bolt-On
15A THQL1115AF2 THHQL1115AF2 THQB1115AF2 THHQB1115AF2
20A THQL1120AF2 THHQL1120AF2 THQB1120AF2 THHQB1120AF2