Ok, well the house is closed up and painted. What would you suggest I do? I have a 14/3 run to the second floor, where 14/2 goes to one room, than 14/2 to another. How can I make these AFCI. I assume the inspector will come in with a AFCI tester to plug into random receptacles?

If I am remembering correctly (this was late spring when it was roughed) I put a j box in the attic and ran the 14/3 homerun to it than split off to 14/2 to each room. I suppose I can eliminate the red on the multi wire and just use one circuit for all. I hate to do it, but if the two pole AFCI breaker will not support the single neutral I dont have a choice.