Originally Posted by Up2code
Correct. Could the grounding busbar in the subpanel be used for this purpose, since it meets the requirements such as being aluminum or copper AND 1/4" by 2" minimum.


the minimum requirement per NEC is 1/4" thick by 2" wide. the grounding bar in the subpanel is not 2" wide.

If you can, just install a bar outside of the panel and connect all of your existing GEC to it.


Be kind to your neighbor, he knows where you live