New main service panelboard with disconnect, was installed in building, which the Grounding Electrode Conductors were terminated in(NEC 2008 250.64(F)(2).
NOW... POCO wants the main service disconnect OUTSIDE the building, per their preference.
Well... doing so would make the indoor, newly installed main service panelboard, with disconnect now a feeder panel. Which will now require removal of MBJ and installation of a seperate equipment grounding conductor from newly required OUTDOOR service disconnect.
QUESTION is now what should be done with the Grounding Electrode Conductors(which now are just bonding jumpers to the different electrodes) that are terminated in what is now the feeder panel.
If a new, Grounding Electrode Conductor were installed from the newly required, outdoor service disconnect...
into what is now the feeder panel....
and terminated on the equipment grounding conductor terminal bar...
would that be in compliance with NEC 2008 250.64(F)(3)?