Originally Posted by Scott35

3: Although the GFPE does not directly scan for Series Arcs, there was evidence in some of the effected 4s Boxes, showing L-G Arcing.

To me, the Termination issues discovered on this Project are very rare scenarios. I had been in the field for at least 24 Years when discovering the Bad Terminations. Prior to this I had uncovered only a few (no more than 5) such situations - only there was a single Termination issue (only One Wirenut in One Box total), and the Wirenut was either an obviously over-used Ideal, Scotchlock, or something in the "El-Cheapo" line...

My Conclusions:


c: The Wirenuts in this case were damaged from excessive Heat, caused by drawing 100% LCL Current through the internal spring mechanism of the Wirenut,

d: Little, if any, Series Arcing was experienced in the Wirenut,


-- Scott



Scott, please allow me a rebuttal here.

a bad connection is the most common malady of the electrical trade,

said bad connections are usually seen as overheated terminations

this can be described as a series event, or a 'glowing contact'

give me free rein in any house wired a generation ago, and i'll wager i'll find you multiple examples

further, a glowing contact can produce incendary levels before an arc occurs

UL has finally come around recently to recognize said glowing contact as a major fire safety consideration

please look at the latest IEEE paper via a Mr Joe Engle, phd, for this>>>

http://www.combinationafci.com/resources/doc_ieee_combination_afci.pdf

thank you


~S~