Getting back to the original question, I think all kitchen counter top receptacles are GFCI because of the number of hand held appliances you use there. I suppose we could go back to the ROP and see what the thinking was. It really showed up in 93. The 90 code still has the "6' from the sink" language but it does say the intent is to only exempt the fixed in place equipment in a FPN.
I think I still have the 93 ROP spinning on a disk somewhere but I don't see it right now. My hard copy library is packed in boxes because of the renovation.