18-30 Log #3561 NEC-P18 Final Action: Accept in Principle
(406.3(D)(4) (New) )
_______________________________________________________________
Submitter: James T. Dollard, Jr., IBEW Local 98
Recommendation: Add a new list item to 406.3(D) as follows:
406.3(D)
(4) Arc-Fault Circuit Interrupters. Arc-Fault circuit-interrupter protected
receptacles shall be provided where replacements are made at receptacle outlets
that are required to be so protected elsewhere in this Code.
Substantiation: The NEC presently addresses receptacle replacement in
406.3(D). This proposal seeks to expand the present receptacle replacement
requirements to include arc fault protected receptacles where required
elsewhere in the NEC. The existing requirement in 406.3(D)(2) requires GFCI
protected receptacles where replacements are made at receptacle outlets that are
required to be so protected elsewhere in the NEC. There is no practical reason
to limit the level of safety provided by AFCI’s to new homes only.
The benefits of 210.12 have been well substantiated over the last few NEC
cycles, but it is highly unlikely that the fire-reducing provisions of 210.12 will
ever result in AFCI protection for existing dwelling units unless branch-circuit
circuit breakers are replaced or the service is upgraded. There is no practical
reason to limit the level of safety provided by an AFCI to new homes only.
This proposal will provide that extra protection for older homes by requiring
the gradual replacement, over time, of non-AFCI-protected receptacles with
new AFCI-protected ones.
Panel Meeting Action: Accept in Principle
Add a new (4) to 406.3(D) as follows:
406.3(D)
(4) Arc-Fault Circuit-Interrupters. Listed combination arc-fault circuitinterrupter
receptacles shall be provided where replacements are made at
receptacle outlets that are required to be so protected elsewhere in this code.
Exception: Unless the receptacle is protected by an upstream AFCI.
Panel Statement: CMP-18 edited the proposed text for clarity.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 9 Negative: 2


Basically if you just replace ONE receptacle in a dwelling (even if George Washington slept there)in family rooms, dining room, living room, parlor, library, den, bedroom, sunroom, recreation room, closet, hallway, or similar room or area you need to make that an AFCI.

First, has that elusive AFCI "device" ever seen the light of day? If not, you have to use the breaker, does this mean you need to do a panel upgrade or add a load side panel of a style that the breaker is available for?

This is NFPA creating a requirement for something that we really have never seen ... again.


Greg Fretwell