Out of curiosity I checked to see what the NEC would say about this "temporary service." Since it was installed on March 2008 as a temporary service that would violate the 90 day time rule of Article 590.3(B) and the way that service cable has been run violates the 10Ft clearance rule of Article 230.24(B)(1). Plus the sight of how the cable's been connected to the meter socket is rather frightening, that's got unsafe written all over it.