Hi,
I dont understand transformer theory at all so it is all a learning experience for me
I now have the data that was monitored:
Main incomer average demand 375kw
Main incomer total 62884 kWh
Phase 1 reading 64130 kWh
Phase 2 reading 59427 kWh
Phase 3 reading 65098 kWh
Poco meter reading 64420 kWh
They state that as the phase 1 reading is so close to the poco meter reading, they have a ct on phase 1 and are multiplying by 3. They state that the difference is within the tolerance of the 2 meters
The poco meter does state 11kv/110v on it. I will check it later.
I may be more confused than ever

Thanks