wire_twister, I think that is all that is fed from this panel also is just the A/C units. One is on a 60 amp 3 phase breaker and the other one is on a 20 amp.
As far as the fuses blowing. That is not the only reason we're changing this service. There are quiet a few other code violations that I didn't mention. The main fuse disconnect that feeds into the traugh didn't have a neutral pulled in with it. One of the 60 amp disconnects also has a 240 volt circuit coming off it that feeds into a 4 11/16 box, where it is spitbolted and feeds (2) 3 wire range recptacles, and they are waiting til this wiring is straighted out so they can add a 3rd. This same disconnect feeds another 8 or ten circuit panel inside the church.
Not to mention the piece of ground rod outside that was laying on the ground, and when the maintenance man stuck it back in the ground it can be easily pulled up. The wires feeding the 150 amp main fused disconnect have had their strands cut out so they would fit in the lugs, also on the main breaker side of it on the outside. So many it would take too long to list them all probably. That is the reason we decided to redo it all. I'll probably go with a 320 amp meter base with dual lugs, if it comes that way in 3 phase, and go to the 3 phase panel for the A/c loads and the other outside loads, then come off the other lugs to feed a 200 amp "mobile home" type panel with the feed through lugs on the bottom. That way there will be room for a few other circuits outside in the future if needed. Anybody see anything wrong with this idea? Thanks, Steve..