JPS, the 120 volt circuits are not what's blowing. They are fortunately on breakers. It was the 60 amp fuses that are feeding other panels. They have a "rats nest" connection on the neutrals in the trough. I may have to run new feeders to one of the panels, once I get the mess cleaned up. The panel may be overloading the fuse. Everythng's "old"; the wiring, disconnects etc.. except the few breaker circuit panels that have been added over the years. As far as the picture goes, unfortunately, my computer does not have the "port" needed to send pictures. My son's my computer expert and we are thinking about upgrading as soon as possible. I guess my main concern now is trying to put a 200 amp single phase breaker ahead of the inside panel out of a 3 phase panel on the outside. Thanks, Steve...