A sub-panel directly below this Service panel is being fed with #2 SER, but there's something amiss...

I got a measurement of 22.5A on the neutral and .7A on the EGC for the sub-feed.

[Linked Image from users.stargate.net]

This shows the SEU cable entering the box, sans connector. Some RX with no connector as well as open KO's.

[Linked Image from users.stargate.net]

Here's the #2 SER Sub-feeder.

[Linked Image from users.stargate.net]

A wide shot for perspective.

[Linked Image from users.stargate.net]

A good close look at the Neutral and EGC Terminal connections!

[Linked Image]

(It was a service call for a sizzling Circuit Breaker)


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI