Violations: Convenience Store Service and Sub-Panel - 11/10/02 09:02 PM
A sub-panel directly below this Service panel is being fed with #2 SER, but there's something amiss...
I got a measurement of 22.5A on the neutral and .7A on the EGC for the sub-feed.
This shows the SEU cable entering the box, sans connector. Some RX with no connector as well as open KO's.
Here's the #2 SER Sub-feeder.
A wide shot for perspective.
A good close look at the Neutral and EGC Terminal connections!
(It was a service call for a sizzling Circuit Breaker)
I got a measurement of 22.5A on the neutral and .7A on the EGC for the sub-feed.
This shows the SEU cable entering the box, sans connector. Some RX with no connector as well as open KO's.
Here's the #2 SER Sub-feeder.
A wide shot for perspective.
A good close look at the Neutral and EGC Terminal connections!
(It was a service call for a sizzling Circuit Breaker)