Hello Ranger- Trumpy is correct in identifying the compressor terminals. There should be three terminals in a ceramic bossthat feed the motor in the hermetic dome(tin can) you can ring these out with an ohmmeter- there should be some ID for run-common-start, if not, the small klixon biscuit(actually a thermal overload) is connected to the common. Place meter lead on any 2 terminals to check for open windings and then check each to compressor housing to check for grounded windings. if you get a resistance form all terminals, and open to ground, then your motor should be intact. If the refrigerator was tipped on its side during the move, it should have been left to stand up for 24 hours before starting to let the oil return to compressor. Is this compressor on bottom or top of cabinet? If it was started too son or with oil out in system, it may be cooked. if your ohmmeter readings are ok, check resistance of overload- should not be open at room temp. if overload shows continuity, then maybe worth a try to get a new relay(other "coil thing"). Good Luck 2 U