"So, then..I was able to retrieve bills that show the PF of the place ranges from .69 to .76 from 12 months ago.
Would you attempt to size PF caps from the .69 to say a .90. That would push the PF from .76 to .97, wouldn't it?"

You need to maintain a PF of 0.90 or better.
Use the kw load at 0.69 and correct to 0.90 or better. Check the load at 0.76 and using the capacitors installed, see what the caps correct the PF at that load.