I have been looking at 410 and 411 and I am not certain that the NEC prohibits low volt fixtures in the bathtub zone.

Yes for certain 410.4(D) says:

Quote
No parts of cord-connected luminaires (fixtures), hanging luminaires (fixtures), lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within.....

But now look at 410.2

Quote
410.2 Application of Other Articles.

Equipment for use in hazardous (classified) locations shall conform to Articles 500 through 517. Lighting systems operating at 30 volts or less shall conform to Article 411.....

Than 411.1

Quote
411.1 Scope.
This article covers lighting systems operating at 30 volts or less and their associated components.

and finally 411.4

Quote
411.4 Locations Not Permitted.
Lighting systems operating at 30 volts or less shall not be installed (1) where concealed or extended through a building wall, unless using a wiring method specified in Chapter 3, or (2) within 3.0 m (10 ft) of pools, spas, fountains, or similar locations, except as permitted by Article 680.

I don't see tubs in that list.

I do not think 410.4(D) applies to low voltage lighting systems.

What do you all think?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts