Welcome to ECN Adam.

Quote
so please, "tear it apart""!

I am not sure you realize what you just asked. [Linked Image]

That is like asking Jerry Springer to get trashy. [Linked Image]

This is a critical crowd here.

OK you asked so I will start with what jumped out at me.

Quote
240.81 Indicating.
Circuit breakers shall clearly indicate whether they are in the open “off” or closed “on” position.
Where circuit breaker handles are operated vertically rather than rotationally or horizontally, the “up” position of the handle shall be the “on” position.


By the way, is your service under the NEC?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts