230-40: Exception No. 1: Buildings with one or more than one occupancy shall be permitted to have one set of service-entrance conductors for each class of service run to each occupancy or group of occupancies.

Each occupancy can have its own set of service conductors. If an occupancy requires more than one class of service it is permitted to have a set of service entrance conductors for ecah class of service. 240-71(a) says that each set of service conductors permitted by 240-30 Ex.#1 shall be permitted to have six disconnect switches. I'm assuming that each meter serves a seperate occupancy.

Sparky66,
Yes, I agree that there is a 110-26 violation here.

don(resqcapt19)


Don(resqcapt19)