Quote
Well,the AC in question had a no.10 pulled to it and the info on nameplate was as follows..23.9 min.ampacity,40min breaker,40 max breaker....could the no.10 have been used?


Absolutely. The nameplate tells you all you need to know. The minimum ampacity, and the maximum breaker size.