And finally, the new distribution panel, partially installed:
All circuits now in place, just waiting for a quick "tidy up" inside (forgot to snap a photo after that, sorry!):
And all finished, other than the inspection labels etc. to go on the outside:
The left-side main and MCB (16 amps) are the off-peak supply for the solitary storage heater.
The other circuits, counting from the right are:
1. 32A Water heater
2. 20A Sockets: front of store & window
3. 20A Sockets: central sales area, kitchen, side storeroom
4. 20A Sockets: counter, rear, office
5. 16A Sockets: tool display & counter
6. 10A Lights: two aisles
7. 10A Lights: third aisle, store, kitchen
8. 10A Lights: behind counter, rear area, office, W.C.
(Sorry, fellow Brits, no ring circuits employed on this job at all!
).
Conductors for the final circuits are 1.5 sq. mm for lights, 2.5 & 4 sq. mm. for sockets (larger size needed in some conduits due to derating for groups), and 4 sq. mm for the water heater.