To finish off the photos, here are just a few I snapped during installation to help show our methods in answer to the request up the thread.
Here's the main bond to the water service.
This is our standard type of pipe earth clamp, used here with 10 sq. mm. cable (roughly equivalent in size to #7 AWG):
Actually, this is one of
two main bonds, since the building still has two water supplies in use from when it was separate units. The bonding cable passes
uncut through the clamp on the first service. (And you don't want to know what state the bonding was in before.....)
Here's a double socket outlet, which as you can see happens to be at the end of a run (it's the one in that rear store/exit area). Our Regs. don't actually require a separate connection between the socket and the backbox so long as at least one of the mounting lugs is fixed, but I always like to fit one anyway. New "harmonized" European colors now, of course:
Here's that same outlet fitted, energized, and being loop tested: