Fittings Underground #98314
05/26/06 05:48 PM
05/26/06 05:48 PM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Can you install threadless compression fittings underground for a RMC installation?


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: Fittings Underground #98315
05/26/06 06:31 PM
05/26/06 06:31 PM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Why not? I've done it before.

Checkout article 344.10 (B) Corrosive Enviroments.

Re: Fittings Underground #98316
05/26/06 06:32 PM
05/26/06 06:32 PM
S
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
...

and 344.42 (A)

Re: Fittings Underground #98317
05/27/06 07:07 AM
05/27/06 07:07 AM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
My thinking is - Just because it listed as suitable for a wet location or corrosive environment does not make it suitable for direct burial.


George Little
Re: Fittings Underground #98318
05/27/06 07:17 AM
05/27/06 07:17 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Quote
334.10(B) Corrosion Environments. RMC, elbows, couplings, and fittings shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosive influences where protected by corrosion protection and judged suitable for the condition.


Is direct burial 'not in direct contact with the earth'?

If not where is the permission to run any RMC or fittings underground?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Fittings Underground #98319
05/27/06 09:36 AM
05/27/06 09:36 AM
G
George Little  Offline OP
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
You got me Bob. Thanks- one of those mental block thngs I guess [Linked Image]

You got your numbers mixed up but I found it.

[This message has been edited by George Little (edited 05-27-2006).]


George Little

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,917
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
sparky 20
Admin 20
Potseal 13
Popular Topics(Views)
243,537 Are you busy
180,340 Re: Forum
170,829 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9734 MB (Peak: 1.1206 MB) Zlib enabled. Server Time: 2018-01-18 14:10:00 UTC