#98314 - 05/26/06 06:48 PM Fittings Underground  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Can you install threadless compression fittings underground for a RMC installation?


George Little

2017 / 2014 NEC & Related Books and Study Guides

#98315 - 05/26/06 07:31 PM Re: Fittings Underground  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Why not? I've done it before.

Checkout article 344.10 (B) Corrosive Enviroments.


#98316 - 05/26/06 07:32 PM Re: Fittings Underground  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
...

and 344.42 (A)


#98317 - 05/27/06 08:07 AM Re: Fittings Underground  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
My thinking is - Just because it listed as suitable for a wet location or corrosive environment does not make it suitable for direct burial.


George Little

#98318 - 05/27/06 08:17 AM Re: Fittings Underground  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Quote
334.10(B) Corrosion Environments. RMC, elbows, couplings, and fittings shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosive influences where protected by corrosion protection and judged suitable for the condition.


Is direct burial 'not in direct contact with the earth'?

If not where is the permission to run any RMC or fittings underground?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#98319 - 05/27/06 10:36 AM Re: Fittings Underground  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
You got me Bob. Thanks- one of those mental block thngs I guess [Linked Image]

You got your numbers mixed up but I found it.

[This message has been edited by George Little (edited 05-27-2006).]


George Little


Member Spotlight
richard
richard
L.I. New York
Posts: 95