ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
600 KW 120/208 3 Phase Y protection
by Yooperup. 07/24/17 12:20 PM
1913 American Electrician's Handbook
by gfretwell. 07/20/17 01:08 PM
Green House wiring
by ghost307. 07/20/17 09:10 AM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 07/18/17 08:06 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
239,359 Are you busy
174,821 Re: Forum
167,210 Need opinion
Who's Online Now
0 registered members (), 53 guests, and 4 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#94025 - 07/01/05 08:57 AM outside hot tub  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 826
NC
Hi, been a while since I was really able to post. My computer had major problems. Seems like I'm back up and running now.
My question. I have a outside hot tub that is about 20 ft. from the breaker panel. If my memory serves me correct, I need to treat this just like a pool and run the feeder in acceptable conduit to the hot tub disconnect. And also the 220 volt motor does not require a GFCI breaker??? And how about a 120 volt recept. minimum 10 ft. from the tub and maximum of 20 ft. on a GFI. I'm seeing this requirement because 680-40 states that the provisions of Part A and Part B shall apply. Thanks .. Steve


2017 / 2014 NEC & Related Books and Study Guides

#94026 - 07/01/05 10:01 AM Re: outside hot tub  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,099
Estero,Fl,usa
Unless this thing has a humongous heater it needs a GFCI starting in 2002. Prior to that it was only "skid pack" spas that needed GFCI.

680.44 Protection.
Except as otherwise provided in this section, the outlet(s) that supplies a self-contained spa or hot tub, a packaged spa or hot tub equipment assembly, or a field-assembled spa or hot tub shall be protected by a ground-fault circuit interrupter.
(A) Listed Units. If so marked, a listed self-contained unit or listed packaged equipment assembly that includes integral ground-fault circuit-interrupter protection for all electrical parts within the unit or assembly (pumps, air blowers, heaters, lights, controls, sanitizer generators, wiring, and so forth) shall be permitted without additional GFCI protection.
(B) Other Units. A field assembled spa or hot tub rated 3 phase or rated over 250 volts or with a heater load of more than 50 amperes shall not require the supply to be protected by a ground-fault circuit interrupter.
(C) Combination Pool and Spa or Hot Tub. A combination pool/hot tub or spa assembly commonly bonded need not be protected by a ground-fault circuit interrupter.

[This message has been edited by gfretwell (edited 07-01-2005).]


Greg Fretwell


Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 14 (0.002s) Memory: 0.7446 MB (Peak: 0.8585 MB) Zlib enabled. Server Time: 2017-07-27 12:40:05 UTC