Gr.Passing Thru Box 250.148 #92079
02/25/05 11:27 AM
02/25/05 11:27 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
250.148 gives the impression that the Equipment ground wire is not required to be connected to the box if the ungrounded conductors pass thru in a metal box. Also all the Code Review books state the same thing. Shouldn't there be a reference in that section dealing with noncondutive raceways and Metal boxes??? Where even If the ungrounded conductors passed thru, the equipment ground Would be required to connected to the box.I know 250.80 & 250.86 covers it. BUT it should be referenced in 250.148 . Any comments on this???

[This message has been edited by Yoopersup (edited 02-25-2005).]

2017 / 2014 NEC & Related Books and Study Guides
Re: Gr.Passing Thru Box 250.148 #92080
02/25/05 07:45 PM
02/25/05 07:45 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
It IS referenced in 250.148, in sections (A) and (B).


Earl
Re: Gr.Passing Thru Box 250.148 #92081
02/26/05 02:24 PM
02/26/05 02:24 PM
E
Elzappr  Offline
Member
Joined: Dec 2001
Posts: 270
Oregon
Yooper, I see what you mean. But I think the essential point of this section is to require continuity of the equipment ground ing conductor. As you noted, 250.80 and .86 covers the issue of requiring equipment grounds in general for metal boxes.

Re: Gr.Passing Thru Box 250.148 #92082
02/26/05 05:43 PM
02/26/05 05:43 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Ernie, I guess if you are using non metallic raceway and metal boxes, and not splicing or terminating in these boxes, I don't see a hazzard. But why would you do that?? If your trying to gain some shielding, you'd be better served by using metal boxes and EMT or conduit. Plus non metallic boxes are cheaper.


George Little
Re: Gr.Passing Thru Box 250.148 #92083
02/26/05 07:18 PM
02/26/05 07:18 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
George
Metal boxes with nonmetalic Conduits are used a lot of times like 2- 4 inch PVC's underground coming up J box then into Building with 2 -4 inch PVCs , And Yes there ia a Hazard if one of the hots rubbed against the side of the box. You then have a hot box . With smaller pipes metal boxs & PVC conduits its not common But with larger pipes it is!

Re: Gr.Passing Thru Box 250.148 #92084
02/26/05 10:54 PM
02/26/05 10:54 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Okay Ernie, guess you win this one. The Yoopers have to win sometime [Linked Image]


George Little

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,604 Are you busy
180,418 Re: Forum
170,874 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.061s Queries: 14 (0.049s) Memory: 0.9741 MB (Peak: 1.1190 MB) Zlib enabled. Server Time: 2018-01-24 01:51:00 UTC