#90878 - 12/16/04 04:41 PM NFPA 70E Annex D Out of Range SCA  
NFGBillgas  Offline
Junior Member
Joined: Dec 2004
Posts: 3
Buffalo, NY USA
NFPA 70E Annex D has calculations D.6.1 and D.6.2 that need a value for F (short-circuit current, kA) to do the calculation. The value has a qualification statement that says (for the range of 16kA to 50 kA). What do we do for values outside of this range, especially for values below the 16kA?


2017 / 2014 NEC & Related Books and Study Guides

#90879 - 12/16/04 07:42 PM Re: NFPA 70E Annex D Out of Range SCA  
rmiell  Offline
Member
Joined: Nov 2000
Posts: 242
La Junta, Co. USA
I must not have the latest standard, since I don't find annexs in my copy (NFPA70E-2000), but I did find the formula you mentioned, along with a statement that theseequations were derived in the IEEE paper by R.L. Doughty, T.E. Neal, and H.L. Floyd, II, "Predicting Incident Energy to Better Manage teh Electric Arc Hazard on 600V Power Distribution Systems", Record of Conference Papers IEEE IAS 45th Annual Petroleum and Chemical Industry Conference, September 28-30, 1998.

Perhaps you could find a copy of this to see if they adress the out of bounds amounts you refer to.

Rick Miell


#90880 - 12/17/04 10:19 AM Re: NFPA 70E Annex D Out of Range SCA  
NFGBillgas  Offline
Junior Member
Joined: Dec 2004
Posts: 3
Buffalo, NY USA
The range statement is found in NFPA 70E 2004.


#90881 - 12/17/04 03:49 PM Re: NFPA 70E Annex D Out of Range SCA  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
NFPA 70E calculation methods have a range of 16 kA - 50 kA. The IEEE 1584 method has a range of 0.7 kA - 106 kA. Generally, when outside of these ranges use Lee's equations.


Ron

#90882 - 12/17/04 05:55 PM Re: NFPA 70E Annex D Out of Range SCA  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
 
Aside — Some might think that the 70E/1584 arc-flash interest is purely 21st-century, but early impetus for this work is a 1982 IEEE paper by electrical engineer Ralph H Lee at www.ieee-pcic.org/archive/The%20oth...20%20Electric%20Arc%20Flash%20Burns.pdf.

He is not to be confused with Dr Raphael C Lee of the Electrical Trauma Research Program at the University of Chicago, http://etrp.bsd.uchicago.edu/areas/overview.html who has been a very notable pioneer in his own right for emergency and long-term severe electrical-burn treatment.


#90883 - 12/17/04 10:44 PM Re: NFPA 70E Annex D Out of Range SCA  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Bjarney,
Thanks for the backup, I didn't explain.


Ron


Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.002s) Memory: 0.7747 MB (Peak: 0.9207 MB) Zlib enabled. Server Time: 2017-04-24 19:11:48 UTC