Peninsula outlets in kitchen #90604
12/02/04 07:02 PM
12/02/04 07:02 PM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
I have a peninsula counter in kitchen, with no cabinets overhead. There is a range in this peninsula. To the left of the range, it is over 2 ft. to the next receptacle, and to the right of the range there is about 18" of counter space. There is a "bar overhang" of about 1 ft. on the other side. If I interpret the code right, I will have to have a receptacle on the left side of the range within 2 ft. The only space that I have is about 2 1/4" above the back splash of the counter top. It's not enough room to safely cut in a box. The back splash is the "curved type" that is part of the counter top itself. Don't won't to try cutting into that. I don't want to buy it if I mess up or have problems"eek" Can a piece of plug mold work here in the small space above the counter top? And also, on the other side where the bar is at, does the space under the "bar overhang" fall under the 6 ft. rule for the beginning of wall space? Since this obviously is meant to be as a serving type bar and not designed for setting furniture etc. is a receptacle required here? Seems like I've been in other houses and seen one is not provided there. Just wondering if the inspector may have missed it or am I missing something in the code? Thanks Steve.

2017 / 2014 NEC & Related Books and Study Guides
Re: Peninsula outlets in kitchen #90605
12/02/04 08:04 PM
12/02/04 08:04 PM
U
u2slow  Offline
Member
Joined: Sep 2003
Posts: 200
Salt Spring, BC, Canada
The last two jobs I was on had issues with kitchen plugs. Neither case was required by code... it just came down to the builder's specs.

The first was a kitchen island. We ended up putting plugs in the millwork just below the countertop on each end.

The second had only about a 4" stub wall on peninsula. Of course the wall wasn't that short on the drawings, but we had to mash in a plug, garb switch, and telephone plug - all sideways - in that little space.

The last thing I've heard of is plugs on the front face of the millwork just below the countertop. (Usually installed for the elderly or disabled.)

Re: Peninsula outlets in kitchen #90606
12/04/04 12:03 PM
12/04/04 12:03 PM
J
JG  Offline
Member
Joined: Mar 2004
Posts: 16
If the counter top has a sink, range, you must have a recepticle on both ends. 210.50
Of course they must be GFI protected. Plug mold would work as long as the the plugs were not facing up.
JG

Re: Peninsula outlets in kitchen #90607
12/04/04 09:18 PM
12/04/04 09:18 PM
G
George  Offline
Member
Joined: Feb 2002
Posts: 375
sparkync ---

Why not ask your inspector if you can have no recepts in that area?

If not, have an engineer sign the plans without the recepts.

Re: Peninsula outlets in kitchen #90608
12/05/04 06:16 AM
12/05/04 06:16 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
u2slow I do not understand this.

Quote
The last two jobs I was on had issues with kitchen plugs. Neither case was required by code... it just came down to the builder's specs.
The first was a kitchen island. We ended up putting plugs in the millwork just below the countertop on each end.


Was the island smaller than 24" x 12"?

Quote
210.52(C)(2) Island Counter Spaces. At least one receptacle outlet shall be installed at each island counter space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater.


Kitchen islands are generally required to have outlets.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Peninsula outlets in kitchen #90609
12/05/04 09:56 PM
12/05/04 09:56 PM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Thanks for the replies. I ended up cutting in one receptacle in the end of the cabinet on the right side of the range, and on the left hand side of the range, I, very carefully cut in a receptacle in the back splash. It was tight, but all went well. Thanks again.. Steve


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,863 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.004s) Memory: 0.9759 MB (Peak: 1.1201 MB) Zlib enabled. Server Time: 2018-01-23 00:06:11 UTC