ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
AreMetal Ladders Ever OK For Electrical Work?
by HotLine1. 01/22/18 07:31 PM
Photocell
by twh. 01/22/18 05:06 PM
VDE 0100 to introduce AFCIs
by sparky. 01/20/18 05:09 PM
MRI LED lights dimmer control replacement - wow!
by Potseal. 01/19/18 08:52 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 6 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
15kv cable conduit fill #90297
11/13/04 09:15 AM
11/13/04 09:15 AM
T
trekkie76  Offline OP
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
Can anyone tell me where I can find dimentsions for 15kv concentric neutral cable? Customer wants it in pipe. It looks like a 500 kcmil cable, but there must be a place in the code book with the measurements for it. any help would be appreciated. Thanks, Gary

2017 / 2014 NEC & Related Books and Study Guides
Re: 15kv cable conduit fill #90298
11/13/04 09:22 AM
11/13/04 09:22 AM
T
trekkie76  Offline OP
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
I found it

Re: 15kv cable conduit fill #90299
11/13/04 10:05 AM
11/13/04 10:05 AM
C
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
It is not recommended to put concentric neutral cable in conduit, it is intended to be direct buried. If you wish to put it in conduit, get jacketed concentric neutral cable. Over the years, we have bad performance from concentric neutral cable in conduit. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
Re: 15kv cable conduit fill #90300
11/14/04 10:18 AM
11/14/04 10:18 AM
T
trekkie76  Offline OP
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
charlie, what performance problems ? We are going to put it in PVC. What do you mean by jacketed, I tought it already had a jacket on it(Black jacket with pinkish insulation inside)? It is listed for direct burial, but the customer wanted it in pipe. If we bury it without pipe, still would need a riser. Would this hurt the wire also? Always good to get advice from the other side of the fence.Thanks, Gary

Re: 15kv cable conduit fill #90301
11/14/04 10:12 PM
11/14/04 10:12 PM
C
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
We have put miles of cross-linked solid dielectric bare concentric neutral in the earth with some in PVC conduit. We have had a lot of failures with the cable in the conduit. We quit using the bare concentric neutral and went to a polyethylene jacket over the concentric neutral cable and have had no trouble with the jacketed concentric neutral cable. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
Re: 15kv cable conduit fill #90302
11/18/04 08:48 PM
11/18/04 08:48 PM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
Charlie,
Did you ever pin point why the cable was failing? The utilities here run it in PVC all the time.

Re: 15kv cable conduit fill #90303
11/18/04 10:11 PM
11/18/04 10:11 PM
C
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
I seem to remember a problem with arcing between the concentric neutral conductors and the outside of the cable.


Charlie Eldridge, Indianapolis Utility Power Guy

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,597 Are you busy
180,402 Re: Forum
170,868 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9831 MB (Peak: 1.1325 MB) Zlib enabled. Server Time: 2018-01-23 06:15:10 UTC