#90297 - 11/13/04 10:15 AM 15kv cable conduit fill  
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
Can anyone tell me where I can find dimentsions for 15kv concentric neutral cable? Customer wants it in pipe. It looks like a 500 kcmil cable, but there must be a place in the code book with the measurements for it. any help would be appreciated. Thanks, Gary


2017 / 2014 NEC & Related Books and Study Guides

#90298 - 11/13/04 10:22 AM Re: 15kv cable conduit fill  
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
I found it


#90299 - 11/13/04 11:05 AM Re: 15kv cable conduit fill  
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
It is not recommended to put concentric neutral cable in conduit, it is intended to be direct buried. If you wish to put it in conduit, get jacketed concentric neutral cable. Over the years, we have bad performance from concentric neutral cable in conduit. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy

#90300 - 11/14/04 11:18 AM Re: 15kv cable conduit fill  
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
charlie, what performance problems ? We are going to put it in PVC. What do you mean by jacketed, I tought it already had a jacket on it(Black jacket with pinkish insulation inside)? It is listed for direct burial, but the customer wanted it in pipe. If we bury it without pipe, still would need a riser. Would this hurt the wire also? Always good to get advice from the other side of the fence.Thanks, Gary


#90301 - 11/14/04 11:12 PM Re: 15kv cable conduit fill  
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
We have put miles of cross-linked solid dielectric bare concentric neutral in the earth with some in PVC conduit. We have had a lot of failures with the cable in the conduit. We quit using the bare concentric neutral and went to a polyethylene jacket over the concentric neutral cable and have had no trouble with the jacketed concentric neutral cable. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy

#90302 - 11/18/04 09:48 PM Re: 15kv cable conduit fill  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
Charlie,
Did you ever pin point why the cable was failing? The utilities here run it in PVC all the time.


#90303 - 11/18/04 11:11 PM Re: 15kv cable conduit fill  
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
I seem to remember a problem with arcing between the concentric neutral conductors and the outside of the cable.


Charlie Eldridge, Indianapolis Utility Power Guy


Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.002s) Memory: 0.7842 MB (Peak: 0.9377 MB) Zlib enabled. Server Time: 2017-07-27 08:33:47 UTC