15kv cable conduit fill #90297 11/13/04 10:15 AM
Joined: Jun 2004
Posts: 220
T
trekkie76 Offline OP
Member
Can anyone tell me where I can find dimentsions for 15kv concentric neutral cable? Customer wants it in pipe. It looks like a 500 kcmil cable, but there must be a place in the code book with the measurements for it. any help would be appreciated. Thanks, Gary

2017 / 2014 NEC & Related Books and Study Guides
Re: 15kv cable conduit fill #90298 11/13/04 10:22 AM
Joined: Jun 2004
Posts: 220
T
trekkie76 Offline OP
Member
I found it

Re: 15kv cable conduit fill #90299 11/13/04 11:05 AM
Joined: Apr 2004
Posts: 201
CharlieE Offline
Member
It is not recommended to put concentric neutral cable in conduit, it is intended to be direct buried. If you wish to put it in conduit, get jacketed concentric neutral cable. Over the years, we have bad performance from concentric neutral cable in conduit. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
Re: 15kv cable conduit fill #90300 11/14/04 11:18 AM
Joined: Jun 2004
Posts: 220
T
trekkie76 Offline OP
Member
charlie, what performance problems ? We are going to put it in PVC. What do you mean by jacketed, I tought it already had a jacket on it(Black jacket with pinkish insulation inside)? It is listed for direct burial, but the customer wanted it in pipe. If we bury it without pipe, still would need a riser. Would this hurt the wire also? Always good to get advice from the other side of the fence.Thanks, Gary

Re: 15kv cable conduit fill #90301 11/14/04 11:12 PM
Joined: Apr 2004
Posts: 201
CharlieE Offline
Member
We have put miles of cross-linked solid dielectric bare concentric neutral in the earth with some in PVC conduit. We have had a lot of failures with the cable in the conduit. We quit using the bare concentric neutral and went to a polyethylene jacket over the concentric neutral cable and have had no trouble with the jacketed concentric neutral cable. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
Re: 15kv cable conduit fill #90302 11/18/04 09:48 PM
Joined: Aug 2001
Posts: 599
N
Nick Offline
Member
Charlie,
Did you ever pin point why the cable was failing? The utilities here run it in PVC all the time.

Re: 15kv cable conduit fill #90303 11/18/04 11:11 PM
Joined: Apr 2004
Posts: 201
CharlieE Offline
Member
I seem to remember a problem with arcing between the concentric neutral conductors and the outside of the cable.


Charlie Eldridge, Indianapolis Utility Power Guy

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,337
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,058 Are you busy
205,042 Re: Forum
193,167 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3