ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Video: Inventor of the GFCI self-testing shocks
by Bill Addiss. 01/17/18 11:11 PM
FPE in Germany
by HotLine1. 01/17/18 07:07 PM
VDE 0100 to introduce AFCIs
by LongRunner. 01/17/18 10:32 AM
Fujifilm Recalls Power Adapter Wall Plugs
by Admin. 01/16/18 07:04 PM
Air Compressor feeder conductor sizing
by Potseal. 01/15/18 09:08 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 22 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
IG and EG in same conduit #89665
10/12/04 04:23 PM
10/12/04 04:23 PM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
if you run two grounds to an IG outlet the IG ground connects to the yolk/strap of the recept....right? egc connects to the box...right?

so do i not need an insulating material between the yolk of the recpt and the metal box to isolate these two systems?

i almost feel guilty getting all this free advice!

thanks for any replies.

-regards

Mustang


Electricity has no respect for ignorance!
2017 / 2014 NEC & Related Books and Study Guides
Re: IG and EG in same conduit #89666
10/12/04 05:01 PM
10/12/04 05:01 PM
C
capt al  Offline
Member
Joined: Jun 2004
Posts: 206
Norton, Ma USA
Mustang, An IG rect already has the yoke insulated from the the IG ground terminal.

Al

Re: IG and EG in same conduit #89667
10/12/04 05:04 PM
10/12/04 05:04 PM
A
Anonymous
Unregistered

Your going to find that you do not have any continuity between the ground screw and the strap on a IG receptacle.

Re: IG and EG in same conduit #89668
10/12/04 05:27 PM
10/12/04 05:27 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Mustang

Do you mind if I ask where the IG originates from?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: IG and EG in same conduit #89669
10/12/04 05:38 PM
10/12/04 05:38 PM
C
capt al  Offline
Member
Joined: Jun 2004
Posts: 206
Norton, Ma USA
Mustang, you are correct about the 2 ground conductors. The IG ground connects to the ground terminal on the rect. The egc connects to the box. Like kentvw said there is no continuity between yoke/strap and rect ground terminal. Do not insulate the yoke from your metal box. A true IG rect already isolates the 2 grounds.

Al

Re: IG and EG in same conduit #89670
10/12/04 05:54 PM
10/12/04 05:54 PM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
Thanks for the replies. I thought that an IG recept came with an insulating spacer attached to each screw..

The IG circuit originates from a IG terminal that is bonded to the neutral at the service Main OCPD..

I appreciate the professional replies.

Sincerely

Mustang


Electricity has no respect for ignorance!
Re: IG and EG in same conduit #89671
10/12/04 06:03 PM
10/12/04 06:03 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Quote
The IG circuit originates from a IG terminal that is bonded to the neutral at the service Main OCPD.


Great, I only asked because it sounded like you where unfamiliar with IGs and many people think think an IG must run to a separate ground rod that is isolated from the buildings grounding electrode system.

Do not be offended, being unfamiliar with something has nothing to do with your abilities. [Linked Image]

I am very unfamiliar with hazardous locations, but IGs I work with all the time. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: IG and EG in same conduit #89672
10/12/04 06:14 PM
10/12/04 06:14 PM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
No offense taken. I have been in the trade 28 years and most of my experience is heavy industrial working around gas turbines and fossil fuel plants.

I am pretty good across the board but I do know everything. I do not mind asking a question if I do not know or if I am not sure.

I used to do a lot of commercial work but it has been a long time.

The electrical trade is about the broadest field there is.

I appreciate the comments and the way they are worded...i have been on jobs where if you did not know how to bend a 4 point saddle or a rolling offset you were considered a romex ranger...i can hold my own in both arenas pretty well. I have run a lot of pipe and i have jerked a lot of romex too!

The guy who claims to know it all is the guy to watch out for!

One thing for sure...you can always count on the expertise, knowledge and experience that is demonstrated on a daily basis on this forum..

I use the forum all the time to verify drawings, field conditions, or when i am planning a job or if i am just stumped..

You never know what is going to come up!

thanks again,

Mustang


Electricity has no respect for ignorance!
Re: IG and EG in same conduit #89673
10/12/04 08:42 PM
10/12/04 08:42 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 925
Regina, Sask.
Quote
I thought that an IG recept came with an insulating spacer attached to each screw
I saw that style of isolation many years ago. More common, I think, is a yoke isolated from the receptacle.

Re: IG and EG in same conduit #89674
10/12/04 08:58 PM
10/12/04 08:58 PM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
so now an isolated ground type recept. has no continuity between the yolk and the IGC?

thats interesting..i will have to take a look at one of them.

it only makes sense since the device is isolating the ground from the other grounded components.

they both have the same potential though since they are bonded at the Main OCPD.

i have seen so-called IG systems that were not connected correctly.

how do you tell if there is another connection to the IG ckt?

are the benefits of an IG to reduce the interference to electronic equipment?

they seem to be called for in commercial and medical facilities.

does the code require an IG recept or ckt anywhere?

thanks for the comments

regards

mustang


Electricity has no respect for ignorance!
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 20
Potseal 13
Popular Topics(Views)
243,539 Are you busy
180,341 Re: Forum
170,831 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.062s Queries: 15 (0.037s) Memory: 1.0228 MB (Peak: 1.1993 MB) Zlib enabled. Server Time: 2018-01-18 21:54:25 UTC