#8919 - 04/09/02 11:17 PM Standard Fuses  
Randy Barnett  Offline
Junior Member
Joined: Apr 2002
Posts: 4
Loveland CO
HI Dan,
Thanks for being here!
240.6 on Standard Ampere Ratings for fuses and fixed-trip cb's is pretty well self-explanatory. But, why a fuse with a standard ampere rating of 601 Amps? Is this a special application of some type?
Thanks in advance!


Work Gear for Electricians and the Trades

#8920 - 04/10/02 09:37 AM Re: Standard Fuses  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Great Q!

I always thought that was a typo... and how could they possibly tell the difference between a 600 and a 601? (Put >601A on it and the 601 will open first?)


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

#8921 - 04/12/02 12:34 PM Re: Standard Fuses  
Dan Neeser  Offline
Member
Joined: Mar 2002
Posts: 29
St. Louis, MO, USA
Randy,

That is probably one of the most asked questions when it comes to fuses. In fact I had the same question last week.

The reason there is a 601 fuse is to give flexibility. Class R and J fuses only go up to 600A. Above 600A, a Class L fuse must be used. Class L fuses range from 601A-6000A. The first case size of a listed Class L fuse is 800A with fuses sizes typically of 601, 650, 700, 750 and 800A.

Thus, if you have a circuit that could be sized at 600A, but may have to be increased in the future due to future expansion or motor inrush issues, Class L is the obvious choice. By going with a 601A Class L fuse, in an 800A disconnect, the fuses could be increased in the future up to 800A, provided conductors with an appropriate ampacity are used.

Thanks,
Dan


#8922 - 04/12/02 11:22 PM Re: Standard Fuses  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Dan,

Thanks, as usual, when one finally understands the "why's", it's easier to remember...

Now it makes sense...

[Linked Image]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI


Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7601 MB (Peak: 0.8919 MB) Zlib enabled. Server Time: 2017-07-21 22:50:32 UTC