Posted By: Randy Barnett Standard Fuses - 04/10/02 03:17 AM
HI Dan,
Thanks for being here!
240.6 on Standard Ampere Ratings for fuses and fixed-trip cb's is pretty well self-explanatory. But, why a fuse with a standard ampere rating of 601 Amps? Is this a special application of some type?
Thanks in advance!
Posted By: sparky66wv Re: Standard Fuses - 04/10/02 01:37 PM
Great Q!

I always thought that was a typo... and how could they possibly tell the difference between a 600 and a 601? (Put >601A on it and the 601 will open first?)
Posted By: Dan Neeser Re: Standard Fuses - 04/12/02 04:34 PM
Randy,

That is probably one of the most asked questions when it comes to fuses. In fact I had the same question last week.

The reason there is a 601 fuse is to give flexibility. Class R and J fuses only go up to 600A. Above 600A, a Class L fuse must be used. Class L fuses range from 601A-6000A. The first case size of a listed Class L fuse is 800A with fuses sizes typically of 601, 650, 700, 750 and 800A.

Thus, if you have a circuit that could be sized at 600A, but may have to be increased in the future due to future expansion or motor inrush issues, Class L is the obvious choice. By going with a 601A Class L fuse, in an 800A disconnect, the fuses could be increased in the future up to 800A, provided conductors with an appropriate ampacity are used.

Thanks,
Dan
Posted By: sparky66wv Re: Standard Fuses - 04/13/02 03:22 AM
Dan,

Thanks, as usual, when one finally understands the "why's", it's easier to remember...