ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Single phase VS three phase generator
by 3nd4. 01/24/18 05:53 AM
AreMetal Ladders Ever OK For Electrical Work?
by HotLine1. 01/22/18 07:31 PM
Photocell
by twh. 01/22/18 05:06 PM
VDE 0100 to introduce AFCIs
by sparky. 01/20/18 05:09 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 4 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Blown Fuse = Service Replacement; Old Code Question #88512
06/14/04 10:02 AM
06/14/04 10:02 AM
R
rlrct  Offline OP
Member
Joined: Jul 2003
Posts: 26
South Windsor, CT
Homeowner's sitting in their weekend cottage and turns on the ceiling fan this past weekend. Fan suddenly stops working - blown fuse. Trace it to low voltage on 1 incoming leg (25 v). LOPOCO comes, pulls the meter. Sure 'nuff, one of the clips in the meter base wasn't tight enough and the connection heated. You can see the discoloration on the underground service lateral where the aluminum conductor heated up. Need to replace the meter base. It turns out the entire service through and including the panelboard will need to be replaced. Why?

The GES, which consists of (1) 1/2" ground rod and a single armored grounding wire (looks like #10), is bonded to the meter base. From the meter, SE cable runs to a 100 amp disconnect. From there, old SE cable runs to the original, screw-in fuse panelboard. There is an unfilled hole in the fuse panel for the original service disconnect where the panel was "converted" from 3-wire service equipment to a 3-wire subpanel. There is an armored grounding cable that runs to the copper water pipe where it's attached within 5' of the water service entrance with a standard, tagged and labelled, clamp. Unfortunately, that conductor to the water pipe is only satisfying 250.104, because about a foot to the right of the clamp, the copper transitions to PVC where it's PVC to and through the foundation.

So, we have:
  • a 100-amp service, with
  • a panelboard with no isolated ground which should be 4-wire,
  • fed by SE cable with no grounded conductor,
  • where the uninsulated grounding conductor is current carrying and connects to
  • a GES which is undersized for the service.


BTW, loads include electric range with double oven, hot water heater and dryer.

Was it ever code-compliant to run just a 3-wire feed from the SD to a panelboard, where the bonding was at/before the SD? Sort of doesn't matter, because the whole mess is being corrected now, but I am curious about the code from the early 1970's when this was done.

Rob

[This message has been edited by rlrct (edited 06-14-2004).]

[This message has been edited by rlrct (edited 06-14-2004).]

2017 / 2014 NEC & Related Books and Study Guides
Re: Blown Fuse = Service Replacement; Old Code Question #88513
06/14/04 12:33 PM
06/14/04 12:33 PM
T
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
If the service disconnectting means is not located in or on the building were that panel is mounted it would still be lawful today to run a three wire cable as the feeder as long as there are no parallel conductve paths betwen the two locations.
--
Tom H


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Re: Blown Fuse = Service Replacement; Old Code Question #88514
06/14/04 12:41 PM
06/14/04 12:41 PM
R
rlrct  Offline OP
Member
Joined: Jul 2003
Posts: 26
South Windsor, CT
This is a single family residence. The service disconnect is on a basement wall (within 5' of the meter). The panelboard is about 12' away on another basement wall.

Re: Blown Fuse = Service Replacement; Old Code Question #88515
06/14/04 05:19 PM
06/14/04 05:19 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
In my experience it never has been allowed by code.


Earl
Re: Blown Fuse = Service Replacement; Old Code Question #88516
06/15/04 02:04 PM
06/15/04 02:04 PM
A
andyp95  Offline
Member
Joined: Mar 2004
Posts: 46
Vermont
IMO the service disconnect should be considered the main,and the 12' away panelboard should be considered a subpanel and be fed with a 4 cond. cable i.e. SER with a bonded ground bar and a seperate isolated nuetral bar.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Popular Topics(Views)
243,607 Are you busy
180,425 Re: Forum
170,876 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9675 MB (Peak: 1.1050 MB) Zlib enabled. Server Time: 2018-01-24 11:48:11 UTC