ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
600 KW 120/208 3 Phase Y protection
by SteveFehr. 07/23/17 09:46 AM
1913 American Electrician's Handbook
by gfretwell. 07/20/17 01:08 PM
Green House wiring
by ghost307. 07/20/17 09:10 AM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 07/18/17 08:06 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
239,259 Are you busy
174,678 Re: Forum
167,086 Need opinion
Who's Online Now
0 registered members (), 61 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#85690 - 07/29/03 06:28 AM Upside down panel?  
Brian Roberts  Offline
Junior Member
Joined: Jul 2003
Posts: 5
I just saw a new house with the circuit breaker panel mounted upside down. The main breaker was on the bottom. Is this allowed?
I was always taught that the line side should be on the top.


2017 / 2014 NEC & Related Books and Study Guides

#85691 - 07/29/03 06:48 AM Re: Upside down panel?  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
I'm not sure about the line-on-top issue, but if the main breaker handle operates vertically, then the upside down mounting would violate 240.81.


#85692 - 07/29/03 09:29 AM Re: Upside down panel?  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Mounting these things upside down is done all the time, generally to keep from running the service entrance conductors from the bottom of the panel to the top. As Paul pointed out, as long as the service disconnect is not upside down, no problem.

You need to forget about line being on top and load being on the bottom, this could be a dangerous assumption For example, a 200 amp breaker with lugs on both ends could have the power coming in the bottom. This would be allowed as long as there are no Line and Load markings on the breaker or the enclosure. You turn off the breaker & assume the lower lugs are de-energized & you could become a statistic. [Linked Image]

Besides which, when you order what many of us consider a real panelboard, not the cheap load centers we usually deal with, you specify if you want top feed or bottom feed.

Tom


[This message has been edited by Tom (edited 07-29-2003).]


Few things are harder to put up with than the annoyance of a good example.

#85693 - 07/29/03 09:49 AM Re: Upside down panel?  
Brian Roberts  Offline
Junior Member
Joined: Jul 2003
Posts: 5
Thanks for clearing that up! The breaker operates sideways. I still don't like to see the embossed breaker numbers with #1 at the bottom and #40 at the top. Maybe I'll just have to get used to it. Thanks again.


#85694 - 07/29/03 09:57 AM Re: Upside down panel?  
GEO  Offline
Member
Joined: Mar 2003
Posts: 47
Lancaster,Pa
2002 240.33 240.81



Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7677 MB (Peak: 0.9074 MB) Zlib enabled. Server Time: 2017-07-23 20:47:16 UTC