250.104(A)(1) #85211
06/06/03 08:07 PM
06/06/03 08:07 PM
Bill Addiss  Offline OP
Member
Joined: Oct 2000
Posts: 3,890
NY, USA
250.104(A)(1) reads:
Quote
General. Metal water piping system(s) installed in or attached to a building or structure shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) used shall be sized in accordance with Table 250.66 except as permitted in 250.104(A)(2) and (A)(3)
Does this, by itself mean that water piping systems shall be bonded to the service equipment enclosure and the grounded conductor at the service?

Or does it mean bonded to either the service equipment enclosure or the grounded conductor at the service?

Bill

2017 / 2014 NEC & Related Books and Study Guides
Re: 250.104(A)(1) #85212
06/06/03 08:46 PM
06/06/03 08:46 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Bill, as far as grammar is concerned, (I don't know if you want to listen to me knowing how I did in grammar) items in sequence divided by commas followed by "and" are in addition to. Items in sequence followed by "or" are optional.

Roger

Re: 250.104(A)(1) #85213
06/06/03 08:56 PM
06/06/03 08:56 PM
T
txsparky  Offline
Member
Joined: May 2001
Posts: 552
Magnolia,.Texas U.S.A.
Roger,
You get an "A+" today !! [Linked Image]


Donnie
Re: 250.104(A)(1) #85214
06/06/03 09:30 PM
06/06/03 09:30 PM
Bill Addiss  Offline OP
Member
Joined: Oct 2000
Posts: 3,890
NY, USA
Roger,

I think you're right.
Do you think that was the intent?

Bill

Re: 250.104(A)(1) #85215
06/07/03 10:48 AM
06/07/03 10:48 AM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Thanks Donnie. [Linked Image] Bill, I would say this was the intent. The part I think should be changed, is "or to the one or more grounding electrodes used". If the GE installation is soley rods and the GEC is #6 we would have a conflict with "the grounding electrode conductor where of sufficient size".

I mean if we bond to the GEC we have to concern ourselves with the size of the GEC but, if we attach to the GE itself the wording would let us ingnore the GEC size.

And on the same point, "The bonding jumper(s) used shall be sized in accordance with Table 250.66 except as permitted in 250.104(A)(2) and (A)(3)" what would this accomplish? [Linked Image]

Roger


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,558 Are you busy
180,361 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.9677 MB (Peak: 1.1051 MB) Zlib enabled. Server Time: 2018-01-20 03:24:00 UTC