AFCI Question #83637
02/10/03 09:15 PM
02/10/03 09:15 PM
P
pip  Offline OP
Member
Joined: Dec 2000
Posts: 15
Little Elm,Tx
In 210.12(B) it says -All branch circuits that supply 125v, single phase, 15 and 20 amp
OUTLETS in berooms shall be protected. My question is is a switch for a light fixture considered an outlet?

2017 / 2014 NEC & Related Books and Study Guides
Re: AFCI Question #83638
02/10/03 09:35 PM
02/10/03 09:35 PM
T
txsparky  Offline
Member
Joined: May 2001
Posts: 552
Magnolia,.Texas U.S.A.
Article 100 Definitions
Outlet-A point on the wiring system at which current is taken to supply utilization equipment.
Not by definition,but if the switch is supplying a fixture in the bedroom it would have to be on the AFCI circuit.

BTW-- Where is Little Elm?

[This message has been edited by txsparky (edited 02-10-2003).]


Donnie
Re: AFCI Question #83639
02/11/03 07:31 AM
02/11/03 07:31 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Actually 210.12 (2002 NEC) requires the AFCI to "provide protection for the entire branch circuit".
It was the '99 code that referred to the "outlets"

Re: AFCI Question #83640
02/11/03 10:42 AM
02/11/03 10:42 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
I still want to konw where I can find an outlet that is rated 125 volts, 15 or 20 amps.
Don


Don(resqcapt19)
Re: AFCI Question #83641
02/11/03 12:02 PM
02/11/03 12:02 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Don,

Check the supplier that provides the 3 phase 115 volt motors listed in Table 430.150! [Linked Image]

Re: AFCI Question #83642
02/11/03 02:28 PM
02/11/03 02:28 PM
E
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
Following on what txsparky said, and a comment I just saw in Mike's latest newsletter, since a switch is not an outlet (definition). . .if the switch inside the bedroom is controlling only load outside the bedroom (say, the outdoor flood lighting, or the closet light), then the branch circuit the switch is in does not require AFCI protection.


Al Hildenbrand
Re: AFCI Question #83643
02/11/03 10:02 PM
02/11/03 10:02 PM
P
pip  Offline OP
Member
Joined: Dec 2000
Posts: 15
Little Elm,Tx
thanks guys...first, the 2002 does refer to 15 and 20 amp outlets 210.12(b). Second, little elm is in the DFW 10 miles from Frisco
and about 25 miles north of Dallas. Fastest growing city in texas by percentage population under 50,000. Thanks for the posts...helped me win an arguement.

Re: AFCI Question #83644
02/12/03 12:13 PM
02/12/03 12:13 PM
E
energy7  Offline
Member
Joined: Jun 2002
Posts: 58
Oxnard, CA, USA
And part of the array of outlets to be protected are the Smokeys (210-8). Can anyone in CMP#2 tell me why?


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,599 Are you busy
180,406 Re: Forum
170,869 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.9903 MB (Peak: 1.1496 MB) Zlib enabled. Server Time: 2018-01-23 16:03:09 UTC