ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 260 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#83637 02/10/03 10:15 PM
Joined: Dec 2000
Posts: 15
P
pip Offline OP
Member
In 210.12(B) it says -All branch circuits that supply 125v, single phase, 15 and 20 amp
OUTLETS in berooms shall be protected. My question is is a switch for a light fixture considered an outlet?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#83638 02/10/03 10:35 PM
Joined: May 2001
Posts: 552
T
Member
Article 100 Definitions
Outlet-A point on the wiring system at which current is taken to supply utilization equipment.
Not by definition,but if the switch is supplying a fixture in the bedroom it would have to be on the AFCI circuit.

BTW-- Where is Little Elm?

[This message has been edited by txsparky (edited 02-10-2003).]


Donnie
#83639 02/11/03 08:31 AM
Joined: Mar 2001
Posts: 2,056
R
Member
Actually 210.12 (2002 NEC) requires the AFCI to "provide protection for the entire branch circuit".
It was the '99 code that referred to the "outlets"

#83640 02/11/03 11:42 AM
Joined: Nov 2000
Posts: 2,148
R
Member
I still want to konw where I can find an outlet that is rated 125 volts, 15 or 20 amps.
Don


Don(resqcapt19)
#83641 02/11/03 01:02 PM
Joined: Mar 2001
Posts: 2,056
R
Member
Don,

Check the supplier that provides the 3 phase 115 volt motors listed in Table 430.150! [Linked Image]

#83642 02/11/03 03:28 PM
Joined: Oct 2001
Posts: 597
E
Member
Following on what txsparky said, and a comment I just saw in Mike's latest newsletter, since a switch is not an outlet (definition). . .if the switch inside the bedroom is controlling only load outside the bedroom (say, the outdoor flood lighting, or the closet light), then the branch circuit the switch is in does not require AFCI protection.


Al Hildenbrand
#83643 02/11/03 11:02 PM
Joined: Dec 2000
Posts: 15
P
pip Offline OP
Member
thanks guys...first, the 2002 does refer to 15 and 20 amp outlets 210.12(b). Second, little elm is in the DFW 10 miles from Frisco
and about 25 miles north of Dallas. Fastest growing city in texas by percentage population under 50,000. Thanks for the posts...helped me win an arguement.

#83644 02/12/03 01:13 PM
Joined: Jun 2002
Posts: 58
E
Member
And part of the array of outlets to be protected are the Smokeys (210-8). Can anyone in CMP#2 tell me why?