#83455 - 01/31/03 09:27 AM parallel equipment ground  
EVAD7  Offline
Member
Joined: Mar 2002
Posts: 37
MN
When running parallel feeders what size equipment ground is used, and do you run this size wire in each pipe?


2017 / 2014 NEC & Related Books and Study Guides

#83456 - 01/31/03 09:45 AM Re: parallel equipment ground  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
A ful sized ground, based on the OCPD setting(Table 250.122) is required for each conduit. Article 250.122 (C)