When running parallel feeders what size equipment ground is used, and do you run this size wire in each pipe?
Posted By:
Redsy
Re: parallel equipment ground
-
01/31/03
01:45 PM
A ful sized ground, based on the OCPD setting(Table 250.122) is required for each conduit. Article 250.122 (C)
©