#80503 - 04/23/02 03:22 PM Safety Switch -- "Dimple" in Lieu of "Hole"  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Can that dimple be drilled out to allow the use of a padlock, while in the "ON" position, especially in a supervised public location like a baseball stadium?

Does anyone know about any legal case that might cover this situation?

[This message has been edited by Joe Tedesco (edited 04-23-2002).]


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#80504 - 04/23/02 05:49 PM Re: Safety Switch -- "Dimple" in Lieu of "Hole"  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
Where opening of a disconnect would create a hazard, I don’t think you could omit the lock. For example, if the switch served lighting indoors or outdoors, operating the switch at night could create a hazard. An open disconnect for a storm-water pump could create a flooding hazard, and may not be evident until an area becomes ‘submersed.’ There are a number of situations where preventing a switch from being operated (opened or closed) at the wrong time could be considered “practical safeguarding of persons and property.”

But then, I wonder if any switch manufacturer provides printed instructions on proper “use” of the dimple?


#80505 - 04/24/02 09:14 AM Re: Safety Switch -- "Dimple" in Lieu of "Hole"  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
[Linked Image]
DIMPLE

[Linked Image]
No Dimple

Which one is permitted?


Joe Tedesco, NEC Consultant


Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7522 MB (Peak: 0.8774 MB) Zlib enabled. Server Time: 2017-04-28 16:01:04 UTC