#80478 - 04/17/02 05:14 PM Old panel question  
Nairb  Offline
Junior Member
Joined: Apr 2002
Posts: 3
Newark, NJ USA
I am changing the breakers in an old GE residential panel that holds TQL breakers.Currently THQL breakers are used to replace these. They snap in place just fine but the hole in the panel cover do not line up just right. My question is, if I trim the extra quarter inch off of the holes to accommodate the breakers will the panel pass inspection? There will be no gap that would allow anything into the interior of the panel.
Thanks for the help
Brian


2017 / 2014 NEC & Related Books and Study Guides

#80479 - 04/17/02 05:50 PM Re: Old panel question  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
NO, I would cite 90.7 in the 2002 NEC --- No alterations can be accepted under any situation or condition. See 110.2


Joe Tedesco, NEC Consultant

#80480 - 04/17/02 06:16 PM Re: Old panel question  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
I'd chime in with an old favorite in conjunction with 110.2 & that is 110.3(B).

If THQL breakers don't appear in the listing or, more likely, on one of the labels in the breaker box that states which breakers can be used, then you shouldn't use them, even if they do plug on without any trouble.

Tom


Few things are harder to put up with than the annoyance of a good example.

#80481 - 04/17/02 06:21 PM Re: Old panel question  
Nairb  Offline
Junior Member
Joined: Apr 2002
Posts: 3
Newark, NJ USA
Thanks that's what I wanted to know