ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
"Esoteric" countries and their wiring practices?
by winston_1. 04/23/19 02:34 PM
Norwegian power?
by Texas_Ranger. 04/20/19 06:27 PM
Welded Copper Connections
by gfretwell. 04/19/19 04:46 PM
Israel
by annemarie1. 04/18/19 02:35 PM
Water heater calculationsSo when I count calculati
by watersparkfalls. 04/13/19 12:43 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 5 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Old panel question #80478
04/17/02 05:14 PM
04/17/02 05:14 PM
N
Nairb  Offline OP
Junior Member
Joined: Apr 2002
Posts: 3
Newark, NJ USA
I am changing the breakers in an old GE residential panel that holds TQL breakers.Currently THQL breakers are used to replace these. They snap in place just fine but the hole in the panel cover do not line up just right. My question is, if I trim the extra quarter inch off of the holes to accommodate the breakers will the panel pass inspection? There will be no gap that would allow anything into the interior of the panel.
Thanks for the help
Brian

2017 / 2014 NEC & Related Books and Study Guides
Re: Old panel question #80479
04/17/02 05:50 PM
04/17/02 05:50 PM
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
NO, I would cite 90.7 in the 2002 NEC --- No alterations can be accepted under any situation or condition. See 110.2


Joe Tedesco, NEC Consultant
Re: Old panel question #80480
04/17/02 06:16 PM
04/17/02 06:16 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
I'd chime in with an old favorite in conjunction with 110.2 & that is 110.3(B).

If THQL breakers don't appear in the listing or, more likely, on one of the labels in the breaker box that states which breakers can be used, then you shouldn't use them, even if they do plug on without any trouble.

Tom


Few things are harder to put up with than the annoyance of a good example.
Re: Old panel question #80481
04/17/02 06:21 PM
04/17/02 06:21 PM
N
Nairb  Offline OP
Junior Member
Joined: Apr 2002
Posts: 3
Newark, NJ USA
Thanks that's what I wanted to know


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,566 Are you busy
190,792 Re: Forum
180,520 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9593 MB (Peak: 1.0924 MB) Zlib enabled. Server Time: 2019-04-25 12:03:34 UTC