#78400 - 09/19/01 08:19 PM GEC Termination  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
When running the grounding electrode conductor to a transformer a really clean way to terminate is to run through the grounding lug that's mounted to the can unspliced on it's way to XO. From the lug to the XO it doubles as the main bonding jumper. I realize that in a lot of cases you could end up with a undersized MBJ especially larger transformers but it works well on the smaller ones. My question is does this violate the listing of the lug it passes completely through? (The one mounted to the case) I have noticed that the conductor tends to loosen easily when applying this method. (for this reason I don't really like it) Using a quad lug on the case and running a separate MBJ is probably a better way. Any thoughts?


2017 / 2014 NEC & Related Books and Study Guides

#78401 - 09/19/01 08:40 PM Re: GEC Termination  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,306
I have 'run-thru' GEC's using siemens LK-2's on strips, no problem whatsoever.


#78402 - 09/20/01 08:29 AM Re: GEC Termination  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
The problem I've had with this has stemmed from the head of the screw that fastens the lug to the enclosure protruding into the path of the conductor. I tried flat head screws, but had to chamfer the hole in the lug to accommodate the screw's bevel (then thought I was probably voiding said lug's listing...no help)

Any more, I just use a 2 conductor lug, and be done with it.


#78403 - 09/21/01 10:55 AM Re: GEC Termination  
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
Quote
Originally posted by Nick:
When running the grounding electrode conductor to a transformer a really clean way to terminate is to run through the grounding lug that's mounted to the can unspliced on it's way to XO. From the lug to the XO it doubles as the main bonding jumper. I realize that in a lot of cases you could end up with a undersized MBJ especially larger transformers but it works well on the smaller ones. My question is [b]does this violate the listing of the lug it passes completely through? (The one mounted to the case) I have noticed that the conductor tends to loosen easily when applying this method. (for this reason I don't really like it) Using a quad lug on the case and running a separate MBJ is probably a better way. Any thoughts?[/B]


Just substitute a listed lay in lug. These are open on one side to permit the insertion of the conductor without needing to feed it through. They have a forked opening in the end opposite the mounting hole.
--
Tom


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

#78404 - 09/24/01 09:41 PM Re: GEC Termination  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
That's a great solve!


#78405 - 10/18/01 07:07 PM Re: GEC Termination  
gary long  Offline
Member
Joined: Feb 2001
Posts: 32
Greeley,Colorado,USA
Dont forget to take a wire brush and scrape that paint off under and around the lug first !!



Member Spotlight
richard
richard
L.I. New York
Posts: 94
Joined: August 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7770 MB (Peak: 0.9225 MB) Zlib enabled. Server Time: 2017-04-26 08:00:47 UTC