GEC Termination #78400 09/19/01 08:19 PM
Joined: Aug 2001
Posts: 599
N
Nick Offline OP
Member
When running the grounding electrode conductor to a transformer a really clean way to terminate is to run through the grounding lug that's mounted to the can unspliced on it's way to XO. From the lug to the XO it doubles as the main bonding jumper. I realize that in a lot of cases you could end up with a undersized MBJ especially larger transformers but it works well on the smaller ones. My question is does this violate the listing of the lug it passes completely through? (The one mounted to the case) I have noticed that the conductor tends to loosen easily when applying this method. (for this reason I don't really like it) Using a quad lug on the case and running a separate MBJ is probably a better way. Any thoughts?

2017 / 2014 NEC & Related Books and Study Guides
Re: GEC Termination #78401 09/19/01 08:40 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
I have 'run-thru' GEC's using siemens LK-2's on strips, no problem whatsoever.

Re: GEC Termination #78402 09/20/01 08:29 AM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
The problem I've had with this has stemmed from the head of the screw that fastens the lug to the enclosure protruding into the path of the conductor. I tried flat head screws, but had to chamfer the hole in the lug to accommodate the screw's bevel (then thought I was probably voiding said lug's listing...no help)

Any more, I just use a 2 conductor lug, and be done with it.

Re: GEC Termination #78403 09/21/01 10:55 AM
Joined: Mar 2001
Posts: 345
T
tdhorne Offline
Member
Quote
Originally posted by Nick:
When running the grounding electrode conductor to a transformer a really clean way to terminate is to run through the grounding lug that's mounted to the can unspliced on it's way to XO. From the lug to the XO it doubles as the main bonding jumper. I realize that in a lot of cases you could end up with a undersized MBJ especially larger transformers but it works well on the smaller ones. My question is [b]does this violate the listing of the lug it passes completely through? (The one mounted to the case) I have noticed that the conductor tends to loosen easily when applying this method. (for this reason I don't really like it) Using a quad lug on the case and running a separate MBJ is probably a better way. Any thoughts?[/B]

Just substitute a listed lay in lug. These are open on one side to permit the insertion of the conductor without needing to feed it through. They have a forked opening in the end opposite the mounting hole.
--
Tom


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Re: GEC Termination #78404 09/24/01 09:41 PM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
That's a great solve!

Re: GEC Termination #78405 10/18/01 07:07 PM
Joined: Feb 2001
Posts: 32
G
gary long Offline
Member
Dont forget to take a wire brush and scrape that paint off under and around the lug first !!


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 236
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,060 Are you busy
205,042 Re: Forum
193,167 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3