Torque Requirements #77707
07/11/01 10:12 AM
07/11/01 10:12 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
How can the electrical inspector be sure that the torque at terminations meets the manufacturers instructions?

Is there some method that can be used to double check the terminations?


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Torque Requirements #77708
07/11/01 10:58 AM
07/11/01 10:58 AM
M
Mike  Offline
Member
Joined: Feb 2001
Posts: 62
Using a torque screwdriver would be the offical way to check for proper torque.
I've seen some inspectors check for connection tightness by pulling on the wire. Other inpsectors use a screwdriver to check for tightness and not torque.

[This message has been edited by Mike (edited 07-11-2001).]

Re: Torque Requirements #77709
07/11/01 12:27 PM
07/11/01 12:27 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
I don't think there is any way that the torque can be checked by the inspector. I have been taught that it is never correct to re-torque a connection. If an inspector would use a torque wrench to check the torque he would be re-torqueing it. The torque specs that are issued by the manufacturers allow for the "cold flow" or relaxation that will occur after the connection is made. The manufacturer's listed torque will provide the proper contact resistance even with the heat cool cycles that will occur with varying loads. If a connection is re-torqued it may become too tight and result in a poor connection at low loads. This would happen to a connection that has been re-torqued and then subjected to a full load. The full load will cause some heating and expansion resulting in additional cold flow. When the load is removed and the conductor cools, the connection may have a higher resistance then it should have. This problem occurs more with wire connections, than with bus bar connections.
A conductor that exhibits evidence of overheating at a termination should be cut off and re-terminated, not just re-torqued.
Don(resqcapt19)


Don(resqcapt19)
Re: Torque Requirements #77710
07/11/01 05:03 PM
07/11/01 05:03 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,344
What ROP is it that will boost tourqe wrench stocks anyway?

Re: Torque Requirements #77711
07/11/01 05:52 PM
07/11/01 05:52 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
We've got a couple of jurisdictions here that the inspectors actually hover over you while you make up connections. If they've been tightened before they get there, they'll make you remove the wire and start over.

Re: Torque Requirements #77712
07/11/01 06:01 PM
07/11/01 06:01 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
electure,
Do they make you cut it off first? This would be about the only way that the torque could be verified, but it would sure be a problem having the inspector there when you are ready to terminate.

sparky,
110-3(b).

Don(resqcapt19)


Don(resqcapt19)
Re: Torque Requirements #77713
07/11/01 06:13 PM
07/11/01 06:13 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
I've got torque wrenches & torque screwdrivers for my own use, but when I do an inspection, I usually don't use them, mainly because I might become liable for any failure of the connection. However, I did run some experiments & found that the average electrician will stop at a value that is about 20% to30% below the listed torque. This was especially noticeable with Square D breakers up to 30 amp.

I know that there is some bus duct that has dual headed bolts, one head snaps off when the proper torque has been reached, maybe some day we'll have the same thing for the rest of the electrical connections, if we can afford it.

I think Don has the right idea about not re-torquing the connections. But, if you had a lot of patience, you could start with a low value & slowly keep adjusting up.

Tom

[This message has been edited by Tom (edited 07-11-2001).]


Few things are harder to put up with than the annoyance of a good example.
Re: Torque Requirements #77714
07/11/01 06:15 PM
07/11/01 06:15 PM
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Anyone know of a "cheap" torque wrench and torque screwdriver?

I priced a Klein Torque screwdriver and was surprised to fine out that a sawzall is cheaper... heck, a Milwaukee Sawzall is cheaper...

Can't seem to find a torque wrench that measures in-lbs, only ft-lbs.

I'd considered about $50 to be reasonable...


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Torque Requirements #77715
07/11/01 06:20 PM
07/11/01 06:20 PM
A
Anonymous
Unregistered

>you could start with a low value & slowly keep adjusting up.
You wouldn't detect over-tightening.

And if the circuit had been energized and heated up at some point, you might over tighten it.

Re: Torque Requirements #77716
07/11/01 08:02 PM
07/11/01 08:02 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
Don.
Yes, they make you cut the end off of the conductor, restrip it, and reconnect it.
They tell you when you pull the permit that the torque insp. is a requirement(via red rubber stamp on approved prints), and if you don't pay attention, S O L, even if it's 1000 MCM. It's only in a few cities.
. The unfortunate part is that in 1 town, the inspector didn't know how to convert from "/lbs to '/lbs.
Most cities only require a letter from the office, stating that you've torqued it to the manufacturer's specs.
Virgil,
. Home Depot(yeah, I know, everybody hates 'em) Husky "/lbs. (from 25 to 250)
about $40. The torque screwdriver is a pain in the $. Napa.

[This message has been edited by electure (edited 07-11-2001).]

Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,601 Are you busy
180,416 Re: Forum
170,871 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.034s Queries: 15 (0.006s) Memory: 1.0245 MB (Peak: 1.2003 MB) Zlib enabled. Server Time: 2018-01-23 19:57:13 UTC