How can the electrical inspector be sure that the torque at terminations meets the manufacturers instructions?

Is there some method that can be used to double check the terminations?


Joe Tedesco, NEC Consultant
Horizontal Ad
#77708 07/11/01 11:58 AM
Joined: Feb 2001
Posts: 62
M
Member
Using a torque screwdriver would be the offical way to check for proper torque.
I've seen some inspectors check for connection tightness by pulling on the wire. Other inpsectors use a screwdriver to check for tightness and not torque.

[This message has been edited by Mike (edited 07-11-2001).]

#77709 07/11/01 01:27 PM
Joined: Nov 2000
Posts: 2,148
R
Member
I don't think there is any way that the torque can be checked by the inspector. I have been taught that it is never correct to re-torque a connection. If an inspector would use a torque wrench to check the torque he would be re-torqueing it. The torque specs that are issued by the manufacturers allow for the "cold flow" or relaxation that will occur after the connection is made. The manufacturer's listed torque will provide the proper contact resistance even with the heat cool cycles that will occur with varying loads. If a connection is re-torqued it may become too tight and result in a poor connection at low loads. This would happen to a connection that has been re-torqued and then subjected to a full load. The full load will cause some heating and expansion resulting in additional cold flow. When the load is removed and the conductor cools, the connection may have a higher resistance then it should have. This problem occurs more with wire connections, than with bus bar connections.
A conductor that exhibits evidence of overheating at a termination should be cut off and re-terminated, not just re-torqued.
Don(resqcapt19)


Don(resqcapt19)
#77710 07/11/01 06:03 PM
Joined: Oct 2000
Posts: 5,393
S
Member
What ROP is it that will boost tourqe wrench stocks anyway?

#77711 07/11/01 06:52 PM
Joined: Dec 2000
Posts: 4,294
Member
We've got a couple of jurisdictions here that the inspectors actually hover over you while you make up connections. If they've been tightened before they get there, they'll make you remove the wire and start over.

#77712 07/11/01 07:01 PM
Joined: Nov 2000
Posts: 2,148
R
Member
electure,
Do they make you cut it off first? This would be about the only way that the torque could be verified, but it would sure be a problem having the inspector there when you are ready to terminate.

sparky,
110-3(b).

Don(resqcapt19)


Don(resqcapt19)
#77713 07/11/01 07:13 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
I've got torque wrenches & torque screwdrivers for my own use, but when I do an inspection, I usually don't use them, mainly because I might become liable for any failure of the connection. However, I did run some experiments & found that the average electrician will stop at a value that is about 20% to30% below the listed torque. This was especially noticeable with Square D breakers up to 30 amp.

I know that there is some bus duct that has dual headed bolts, one head snaps off when the proper torque has been reached, maybe some day we'll have the same thing for the rest of the electrical connections, if we can afford it.

I think Don has the right idea about not re-torquing the connections. But, if you had a lot of patience, you could start with a low value & slowly keep adjusting up.

Tom

[This message has been edited by Tom (edited 07-11-2001).]


Few things are harder to put up with than the annoyance of a good example.
Horizontal Ad
#77714 07/11/01 07:15 PM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Anyone know of a "cheap" torque wrench and torque screwdriver?

I priced a Klein Torque screwdriver and was surprised to fine out that a sawzall is cheaper... heck, a Milwaukee Sawzall is cheaper...

Can't seem to find a torque wrench that measures in-lbs, only ft-lbs.

I'd considered about $50 to be reasonable...


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#77715 07/11/01 07:20 PM
A
Anonymous
Unregistered
>you could start with a low value & slowly keep adjusting up.
You wouldn't detect over-tightening.

And if the circuit had been energized and heated up at some point, you might over tighten it.

#77716 07/11/01 09:02 PM
Joined: Dec 2000
Posts: 4,294
Member
Don.
Yes, they make you cut the end off of the conductor, restrip it, and reconnect it.
They tell you when you pull the permit that the torque insp. is a requirement(via red rubber stamp on approved prints), and if you don't pay attention, S O L, even if it's 1000 MCM. It's only in a few cities.
. The unfortunate part is that in 1 town, the inspector didn't know how to convert from "/lbs to '/lbs.
Most cities only require a letter from the office, stating that you've torqued it to the manufacturer's specs.
Virgil,
. Home Depot(yeah, I know, everybody hates 'em) Husky "/lbs. (from 25 to 250)
about $40. The torque screwdriver is a pain in the $. Napa.

[This message has been edited by electure (edited 07-11-2001).]

Page 1 of 3 1 2 3

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
BigB 6
timmp 2
Popular Topics(Views)
329,530 Are you busy
254,376 Re: Forum
236,838 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5